      Sailing Anarchy is a very lightly moderated site. This is by design, to afford a more free atmosphere for discussion. There are plenty of sailing forums you can go to where swearing isn't allowed, confrontation is squelched and, and you can have a moderator finger-wag at you for your attitude. SA tries to avoid that and allow for more adult behavior without moderators editing your posts and whacking knuckles with rulers. We don't have a long list of published "thou shalt nots" either, and this is by design. Too many absolute rules paints us into too many corners. So check the Terms of Service - there IS language there about certain types of behavior that is not permitted. We interpret that lightly and permit a lot of latitude, but we DO reserve the right to take action when something is too extreme to tolerate (too racist, graphic, violent, misogynistic, etc.). Yes, that is subjective, but it allows us discretion. Avoiding a laundry list of rules allows for freedom; don't abuse it. However there ARE a few basic rules that will earn you a suspension, and apparently a brief refresher is in order. 1) Allegations of pedophilia - there is no tolerance for this. So if you make allegations, jokes, innuendo or suggestions about child molestation, child pornography, abuse or inappropriate behavior with minors etc. about someone on this board you will get a time out. This is pretty much automatic; this behavior can have real world effect and is not acceptable. Obviously the subject is not banned when discussion of it is apropos, e.g. talking about an item in the news for instance. But allegations or references directed at or about another poster is verboten. 2) Outing people - providing real world identifiable information about users on the forums who prefer to remain anonymous. Yes, some of us post with our real names - not a problem to use them. However many do NOT, and if you find out someone's name keep it to yourself, first or last. This also goes for other identifying information too - employer information etc. You don't need too many pieces of data to figure out who someone really is these days. Depending on severity you might get anything from a scolding to a suspension - so don't do it. I know it can be confusing sometimes for newcomers, as SA has been around almost twenty years and there are some people that throw their real names around and their current Display Name may not match the name they have out in the public. But if in doubt, you don't want to accidentally out some one so use caution, even if it's a personal friend of yours in real life. 3) Posting While Suspended - If you've earned a timeout (these are fairly rare and hard to get), please observe the suspension. If you create a new account (a "Sock Puppet") and return to the forums to post with it before your suspension is up you WILL get more time added to your original suspension and lose your Socks. This behavior may result a permanent ban, since it shows you have zero respect for the few rules we have and the moderating team that is tasked with supporting them. Check the Terms of Service you agreed to; they apply to the individual agreeing, not the account you created, so don't try to Sea Lawyer us if you get caught. Just don't do it. Those are the three that will almost certainly get you into some trouble. IF YOU SEE SOMEONE DO ONE OF THESE THINGS, please do the following: Refrain from quoting the offending text, it makes the thread cleanup a pain in the rear Press the Report button; it is by far the best way to notify Admins as we will get e-mails. Calling out for Admins in the middle of threads, sending us PM's, etc. - there is no guarantee we will get those in a timely fashion. There are multiple Moderators in multiple time zones around the world, and anyone one of us can handle the Report and all of us will be notified about it. But if you PM one Mod directly and he's off line, the problem will get dealt with much more slowly. Other behaviors that you might want to think twice before doing include: Intentionally disrupting threads and discussions repeatedly. Off topic/content free trolling in threads to disrupt dialog Stalking users around the forums with the intent to disrupt content and discussion Repeated posting of overly graphic or scatological porn content. There are plenty web sites for you to get your freak on, don't do it here. And a brief note to Newbies... No, we will not ban people or censor them for dropping F-bombs on you, using foul language, etc. so please don't report it when one of our members gives you a greeting you may find shocking. We do our best not to censor content here and playing swearword police is not in our job descriptions. Sailing Anarchy is more like a bar than a classroom, so handle it like you would meeting someone a little coarse - don't look for the teacher. Thanks.

Archived

This topic is now archived and is closed to further replies.

Point Break

Any Real Electricians Out THere?

22 posts in this topic

Okay, long story short, I'm not an electrician but I play one on TV. Today I'm pretending to be one in my attic.....but I'm not exactly uninformed on the subject either. So.............I just replaced my thousand year old 80 amp panel.......yep 80........with a 200 amp. I'm pulling some new circuits and am taking advantage of existing conduit. I can't get to the top plate to put in any new conduit where the panel is located because of the roof-line angle.....even if I was willing to open the wall.....which I'm not. I have a mix of 1/2" & 3/4" FMC conduit. Just one of them (a 3/4") has 3 existing THHN #10. I'm pulling THHN #12 for each new circuit. I can find plenty of charts for max conduit fill using all same size conductors, but I can't find any charts for how to calculate max fill for mixed size conductors in the same conduit. I'm not interested in jamming them to the max but I want to make sure I keep within the code requirements and safe operation.

 

Any resources/help?

Share this post


Link to post
Share on other sites

It's a heat thing. the reason to not overfill the conduit is to stop the conduit and wires gettin too hot.

 

"I can find plenty of charts for max conduit fill using all same size conductors"

 

If you can figgure out how full the conduit will be with this information. ie 2/3. You should be good to go.

Share this post


Link to post
Share on other sites

It's a heat thing. the reason to not overfill the conduit is to stop the conduit and wires gettin too hot.

 

"I can find plenty of charts for max conduit fill using all same size conductors"

 

If you can figgure out how full the conduit will be with this information. ie 2/3. You should be good to go.

Understood, I get the heat thing (one of the prime reasons I don't want to overfill) but I figure there must be some formula to cover the conversion. I don't want to waste space as I have limited number of conduit, can't get any more in, and want to maximize the circuits I can pull. Where's all these frigging engineers when you need em!!!

 

;)

Share this post


Link to post
Share on other sites

It's a heat thing. the reason to not overfill the conduit is to stop the conduit and wires gettin too hot.

 

"I can find plenty of charts for max conduit fill using all same size conductors"

 

If you can figgure out how full the conduit will be with this information. ie 2/3. You should be good to go.

Understood, I get the heat thing (one of the prime reasons I don't want to overfill) but I figure there must be some formula to cover the conversion. I don't want to waste space as I have limited number of conduit, can't get any more in, and want to maximize the circuits I can pull. Where's all these frigging engineers when you need em!!!

 

;)

 

France? :ph34r:

 

I can check with my brother-the-electrician tomorrow, but iirc you can only fill the conduit 40%, look up the crossection of the wires, add them together and subtract from the conduit, bob's your uncle.

Share this post


Link to post
Share on other sites

It's a heat thing. the reason to not overfill the conduit is to stop the conduit and wires gettin too hot.

 

"I can find plenty of charts for max conduit fill using all same size conductors"

 

If you can figgure out how full the conduit will be with this information. ie 2/3. You should be good to go.

Understood, I get the heat thing (one of the prime reasons I don't want to overfill) but I figure there must be some formula to cover the conversion. I don't want to waste space as I have limited number of conduit, can't get any more in, and want to maximize the circuits I can pull. Where's all these frigging engineers when you need em!!!

 

;)

 

France? :ph34r:

 

I can check with my brother-the-electrician tomorrow, but iirc you can only fill the conduit 40%, look up the crossection of the wires, add them together and subtract from the conduit, bob's your uncle.

Not a bad approach. I'll give that a try. You sure about the 40% cross sectional area? Seems kinda on the light side to me.

 

Thanks for checking BTW. ;)

Share this post


Link to post
Share on other sites

You aren't going to be pulling much more than that anyway, do the existing wires have to be 10ga? might be easier to pull everything out and pull all new wires through the conduit into the junction box in the attic if you can downsize you can get more wires, even if you can't, pulling all new is a hell of a lot easier than trying to pull past existing, especially if you are trying to max out capacity. get some pulling lube, you will need it. B) That just sounds dirty. :P

Share this post


Link to post
Share on other sites

You aren't going to be pulling much more than that anyway, do the existing wires have to be 10ga? might be easier to pull everything out and pull all new wires through the conduit into the junction box in the attic if you can downsize you can get more wires, even if you can't, pulling all new is a hell of a lot easier than trying to pull past existing, especially if you are trying to max out capacity. get some pulling lube, you will need it. B) That just sounds dirty. :P

Its hard to pull out perfectly good #10...........never know when I might need em. I have most of the wires pulled. :huh:

 

I left a bit of room in the one in question. I have 3 #10 and 6 #12 in there right now. Looks at about 2/3's cross sectional area.

Share this post


Link to post
Share on other sites

You can do the calc the fill method. FMC at 40% fill is 0.213 square inches. Wire size depends on the insulation, THHN is common, with #12 is 0.0133 sqin and #10 is 0.0211 sqin. You should be able to find the insulation type on the wire and then look up what your actual area is.

 

Another method that I use often is to use Annex C in the NEC. It lists how many wires of a size and insulation type you can fit in a particular type of conduit. So FMC is actually table C.3 and using THHN insulation again, I can fit 10 #10's or 16 #12's in a 3/4" conduit. So, based off of that, you should be able to fit the #12's in there no problem.

Share this post


Link to post
Share on other sites

Easy work around would be treat all your conductors as #10 and do conduit fill based on that. You'll be under the fill limit easy.

 

Don't forget any grounds you may pull count as fill. And you should have at least one in there to your first jb.

Share this post


Link to post
Share on other sites

Old Indian Trick

 

remove roof tiles above panel - open roof sheathing

 

drill down from above & run new conduit or just romex if all unexposed

 

Oh and then patch roof

 

so it does Not look like a patch cool.gif

Share this post


Link to post
Share on other sites

You can do the calc the fill method. FMC at 40% fill is 0.213 square inches. Wire size depends on the insulation, THHN is common, with #12 is 0.0133 sqin and #10 is 0.0211 sqin. You should be able to find the insulation type on the wire and then look up what your actual area is.

 

Another method that I use often is to use Annex C in the NEC. It lists how many wires of a size and insulation type you can fit in a particular type of conduit. So FMC is actually table C.3 and using THHN insulation again, I can fit 10 #10's or 16 #12's in a 3/4" conduit. So, based off of that, you should be able to fit the #12's in there no problem.

Talk dirty to me, Baby!

Share this post


Link to post
Share on other sites

Easy work around would be treat all your conductors as #10 and do conduit fill based on that. You'll be under the fill limit easy.

 

Don't forget any grounds you may pull count as fill. And you should have at least one in there to your first jb.

Yes on the ground. Pulling a ground in each conduit.. Pulling enough neutrals to share two circuits per return (opposite phases of course).

Share this post


Link to post
Share on other sites

Old Indian Trick

 

remove roof tiles above panel - open roof sheathing

 

drill down from above & run new conduit or just romex if all unexposed

 

Oh and then patch roof

 

so it does Not look like a patch cool.gif

Standing seam metal roof. That won't work my old Indian friend. :lol:

Share this post


Link to post
Share on other sites

holy cow, CA allows your panel to be in such a place... no way in dallas.. good luck..

Share this post


Link to post
Share on other sites

holy cow, CA allows your panel to be in such a place... no way in dallas.. good luck..

House built in 1958. Existing non-conforming probably. No location fuss on the permit.

Share this post


Link to post
Share on other sites

hire an electrician , so if your house burns down , your insurance will pay up, if you do it on your own they may not

Share this post


Link to post
Share on other sites

hire an electrician , so if your house burns down , your insurance will pay up, if you do it on your own they may not

 

 

He works for the fire dept...there are fringe benefits... :rolleyes:

 

 

When I relocated and upgraded my panel, I ran 2 1" conduits to a junction box in the attic, little bit of extra work initially, but...

Share this post


Link to post
Share on other sites

holy cow, CA allows your panel to be in such a place... no way in dallas.. good luck..

 

 

Low rise roof, 8" max at the eaves to fish a conduit through, do-able, but...

Share this post


Link to post
Share on other sites

You aren't going to be pulling much more than that anyway, do the existing wires have to be 10ga? might be easier to pull everything out and pull all new wires through the conduit into the junction box in the attic if you can downsize you can get more wires, even if you can't, pulling all new is a hell of a lot easier than trying to pull past existing, especially if you are trying to max out capacity. get some pulling lube, you will need it. B) That just sounds dirty. :P

Its hard to pull out perfectly good #10...........never know when I might need em. I have most of the wires pulled. :huh:

 

I left a bit of room in the one in question. I have 3 #10 and 6 #12 in there right now. Looks at about 2/3's cross sectional area.

so you have 9 wires in a 3/4" pipe

 

if memory serves you get 15 #12 wires and 9#10's your mixing so your can't get the max of either you can probably pull 3 more #12 wires through and that would be about it. I would watch the amperage and average loads though(for a house it should be fine as long as you aren't putting a full kitchen through it.

Share this post


Link to post
Share on other sites

 

Buzzkill

 

 

Doesn't help, that is for same size conductors. Of course a real man would have ripped out the 3/4 and run a couple of 1 1/2 flex conduits while the box was out (insert Tim the Toolman grunting here). B) Why not punch some holes in the header and push some romex into the attic for the current extra circuits? Leave the space in the conduit for future expansion.

Share this post


Link to post