Posted 21 July 2012 - 09:06 PM
"I can find plenty of charts for max conduit fill using all same size conductors"
If you can figgure out how full the conduit will be with this information. ie 2/3. You should be good to go.
#3
Posted 21 July 2012 - 09:21 PM
Understood, I get the heat thing (one of the prime reasons I don't want to overfill) but I figure there must be some formula to cover the conversion. I don't want to waste space as I have limited number of conduit, can't get any more in, and want to maximize the circuits I can pull. Where's all these frigging engineers when you need em!!!It's a heat thing. the reason to not overfill the conduit is to stop the conduit and wires gettin too hot.
"I can find plenty of charts for max conduit fill using all same size conductors"
If you can figgure out how full the conduit will be with this information. ie 2/3. You should be good to go.
#4
Posted 21 July 2012 - 09:34 PM
Understood, I get the heat thing (one of the prime reasons I don't want to overfill) but I figure there must be some formula to cover the conversion. I don't want to waste space as I have limited number of conduit, can't get any more in, and want to maximize the circuits I can pull. Where's all these frigging engineers when you need em!!!
It's a heat thing. the reason to not overfill the conduit is to stop the conduit and wires gettin too hot.
"I can find plenty of charts for max conduit fill using all same size conductors"
If you can figgure out how full the conduit will be with this information. ie 2/3. You should be good to go.
France?
I can check with my brother-the-electrician tomorrow, but iirc you can only fill the conduit 40%, look up the crossection of the wires, add them together and subtract from the conduit, bob's your uncle.
#5
Posted 21 July 2012 - 10:18 PM
Not a bad approach. I'll give that a try. You sure about the 40% cross sectional area? Seems kinda on the light side to me.
Understood, I get the heat thing (one of the prime reasons I don't want to overfill) but I figure there must be some formula to cover the conversion. I don't want to waste space as I have limited number of conduit, can't get any more in, and want to maximize the circuits I can pull. Where's all these frigging engineers when you need em!!!
It's a heat thing. the reason to not overfill the conduit is to stop the conduit and wires gettin too hot.
"I can find plenty of charts for max conduit fill using all same size conductors"
If you can figgure out how full the conduit will be with this information. ie 2/3. You should be good to go.
France?![]()
I can check with my brother-the-electrician tomorrow, but iirc you can only fill the conduit 40%, look up the crossection of the wires, add them together and subtract from the conduit, bob's your uncle.
Thanks for checking BTW.
#6
Posted 21 July 2012 - 10:24 PM
#7
Posted 21 July 2012 - 10:38 PM
Its hard to pull out perfectly good #10...........never know when I might need em. I have most of the wires pulled.You aren't going to be pulling much more than that anyway, do the existing wires have to be 10ga? might be easier to pull everything out and pull all new wires through the conduit into the junction box in the attic if you can downsize you can get more wires, even if you can't, pulling all new is a hell of a lot easier than trying to pull past existing, especially if you are trying to max out capacity. get some pulling lube, you will need it.
That just sounds dirty.
I left a bit of room in the one in question. I have 3 #10 and 6 #12 in there right now. Looks at about 2/3's cross sectional area.
#8
Posted 22 July 2012 - 12:27 AM
Another method that I use often is to use Annex C in the NEC. It lists how many wires of a size and insulation type you can fit in a particular type of conduit. So FMC is actually table C.3 and using THHN insulation again, I can fit 10 #10's or 16 #12's in a 3/4" conduit. So, based off of that, you should be able to fit the #12's in there no problem.
#9
Posted 22 July 2012 - 01:24 AM
Don't forget any grounds you may pull count as fill. And you should have at least one in there to your first jb.
#10
Posted 22 July 2012 - 01:37 AM
remove roof tiles above panel - open roof sheathing
drill down from above & run new conduit or just romex if all unexposed
Oh and then patch roof
so it does Not look like a patch
#11
Posted 22 July 2012 - 01:42 AM
Talk dirty to me, Baby!You can do the calc the fill method. FMC at 40% fill is 0.213 square inches. Wire size depends on the insulation, THHN is common, with #12 is 0.0133 sqin and #10 is 0.0211 sqin. You should be able to find the insulation type on the wire and then look up what your actual area is.
Another method that I use often is to use Annex C in the NEC. It lists how many wires of a size and insulation type you can fit in a particular type of conduit. So FMC is actually table C.3 and using THHN insulation again, I can fit 10 #10's or 16 #12's in a 3/4" conduit. So, based off of that, you should be able to fit the #12's in there no problem.
#12
Posted 22 July 2012 - 03:30 AM
Yes on the ground. Pulling a ground in each conduit.. Pulling enough neutrals to share two circuits per return (opposite phases of course).Easy work around would be treat all your conductors as #10 and do conduit fill based on that. You'll be under the fill limit easy.
Don't forget any grounds you may pull count as fill. And you should have at least one in there to your first jb.
#13
Posted 22 July 2012 - 03:32 AM
Standing seam metal roof. That won't work my old Indian friend.Old Indian Trick
remove roof tiles above panel - open roof sheathing
drill down from above & run new conduit or just romex if all unexposed
Oh and then patch roof
so it does Not look like a patch
#14
Posted 22 July 2012 - 03:34 AM
#15
Posted 22 July 2012 - 03:44 AM
House built in 1958. Existing non-conforming probably. No location fuss on the permit.holy cow, CA allows your panel to be in such a place... no way in dallas.. good luck..
#16
Posted 22 July 2012 - 03:49 AM
#17
Posted 22 July 2012 - 04:26 AM
hire an electrician , so if your house burns down , your insurance will pay up, if you do it on your own they may not
He works for the fire dept...there are fringe benefits...
When I relocated and upgraded my panel, I ran 2 1" conduits to a junction box in the attic, little bit of extra work initially, but...
#18
Posted 22 July 2012 - 04:29 AM
holy cow, CA allows your panel to be in such a place... no way in dallas.. good luck..
Low rise roof, 8" max at the eaves to fish a conduit through, do-able, but...
#19
Posted 22 July 2012 - 11:41 AM
so you have 9 wires in a 3/4" pipeIts hard to pull out perfectly good #10...........never know when I might need em. I have most of the wires pulled.
You aren't going to be pulling much more than that anyway, do the existing wires have to be 10ga? might be easier to pull everything out and pull all new wires through the conduit into the junction box in the attic if you can downsize you can get more wires, even if you can't, pulling all new is a hell of a lot easier than trying to pull past existing, especially if you are trying to max out capacity. get some pulling lube, you will need it.That just sounds dirty.
![]()
I left a bit of room in the one in question. I have 3 #10 and 6 #12 in there right now. Looks at about 2/3's cross sectional area.
if memory serves you get 15 #12 wires and 9#10's your mixing so your can't get the max of either you can probably pull 3 more #12 wires through and that would be about it. I would watch the amperage and average loads though(for a house it should be fine as long as you aren't putting a full kitchen through it.
#22
Posted 22 July 2012 - 03:15 PM
Buzzkill
Doesn't help, that is for same size conductors. Of course a real man would have ripped out the 3/4 and run a couple of 1 1/2 flex conduits while the box was out (insert Tim the Toolman grunting here).